Why am I limited to 16amps with my 7kw wall charger?
Hi
I’ve got a teathered pod point 7kw wall charger installed. My first charge appeared to pull 30amps and the car charges up quickly. However since then I appear to only be getting 16amps and I can’t work out why. I thought I should get up to 32amps. Things I’ve checked: - BMW App says 16amps while charging - Dashboard says 16amps while charging - I’ve checked the AC limit is at the maximum 32amps - The charging window is set to 00:00 to 23:59 but is unchecked ie I’m able to charge day and night - There don’t appear to be any errors showing anywhere on the car or in the pod point app - The outside temperature has been up to around 11°c. The car has been left on charge for long periods but doesn’t seem to get any faster I’m convinced I’m doing something wrong. Any ideas? |
02-05-2022, 01:36 AM | #2 |
Private
6
Rep 65
Posts |
Are you sure you got 32 amps the first time?
It sounds like everything is setup OK, so it’s either the car limiting it or the wall charger. My wall charger has settings which are set by the installer and depend on the main fuse size of the house supply. I think only houses with a 100 amp fuse will get a charger set to 32 amp. I’m not an electrician or installer, this is just what I read on the installation manual for my charger. |
Appreciate
0
|
02-05-2022, 02:59 AM | #3 |
Private First Class
32
Rep 121
Posts |
This thread has some good points to think about:
https://www.speakev.com/threads/podp...r-slow.160867/ |
Appreciate
0
|
02-05-2022, 04:16 AM | #4 | |
New Member
2
Rep 14
Posts |
Quote:
|
|
Appreciate
0
|
02-05-2022, 04:22 AM | #5 | |
New Member
2
Rep 14
Posts |
Quote:
|
|
Appreciate
0
|
02-07-2022, 04:22 AM | #6 |
New Member
2
Rep 14
Posts |
I called Pod Point this morning and sure enough it was something to do with the way the charge point was configured. They reset it and I’m now back to pulling 6.8kwh / 30 amps. Still not sure why that isn’t 32 amps but I’m not too worried about that.
|
Appreciate
0
|
02-07-2022, 07:17 AM | #7 |
First Lieutenant
234
Rep 366
Posts |
I had the exact same issue with my PodPoint, my installer configured it to be 7.2kW but when Pod-Point remotely comissioned it and updated the software they reset it to 3.6kW. Took a call to Pod-Point to get it set back to 7.2kW.
|
Appreciate
0
|
02-08-2022, 03:33 PM | #8 |
Captain
102
Rep 601
Posts |
Most of them have load monitors upstream, if you only have a 60amp main fuse then it's probably limiting you to protect the fuse due to other draw, it's designed to try leave headroom for spike draw types like ovens drier and washing machines etc
|
Appreciate
0
|
02-09-2022, 05:25 AM | #9 |
New Member
2
Rep 14
Posts |
I asked them the question about 30 v 32 amps. This is the response:
Configuring he unit to 32A has many implications: 1. Most MCB/RCBO manufacturers specify an 80% de-rating factor to prevent unintentional tripping where the the consumer unit is fully loaded (heat adjacent devices produces a reduced rating), the trip limit of a 40A may fall to 32A. 2. EV's are allowed to exceed the maximum rate of charge by 10% (32A EV could charge at 35A), this pushes the Relay rating we use (35A) to the limit and the cable feeding the EVSE in some cases. 3. The Heat Losses in cables increase. 4. Lastly, BS7671 states a maximum rating of 32A for a socket outlet in a domestic environment, if it is known we will be exceeding this limit I believe planning permission must be granted. The Pod Point chargers have proven reliable at 30A unlike other major manufacturers of EVSE in the UK who have in the past used 32A settings. (their relays have failed dangerously), also the mains voltage difference between Europe and the UK does result in the overall charging rate of UK units being higher! (Europe 220V x 32A = 7.04kW, UK 240V x 30A = 7.2kW). The unit to 32A has many implications: 1. Most MCB/RCBO manufacturers specify an 80% de-rating factor to prevent unintentional tripping where the the consumer unit is fully loaded (heat adjacent devices produces a reduced rating), the trip limit of a 40A may fall to 32A. 2. EV's are allowed to exceed the maximum rate of charge by 10% (32A EV could charge at 35A), this pushes the Relay rating we use (35A) to the limit and the cable feeding the EVSE in some cases. 3. The Heat Losses in cables increase. 4. Lastly, BS7671 states a maximum rating of 32A for a socket outlet in a domestic environment, if it is known we will be exceeding this limit I believe planning permission must be granted. The Pod Point chargers have proven reliable at 30A unlike other major manufacturers of EVSE in the UK who have in the past used 32A settings. (their relays have failed dangerously), also the mains voltage difference between Europe and the UK does result in the overall charging rate of UK units being higher! (Europe 220V x 32A = 7.04kW, UK 240V x 30A = 7.2kW). |
Appreciate
0
|
02-09-2022, 07:27 AM | #10 | |
Captain
405
Rep 840
Posts |
Quote:
Hence why the single phase chargers are rated at 7.4kW (230V x 32A = 7.36kW). |
|
Appreciate
0
|
02-09-2022, 08:04 AM | #11 |
First Lieutenant
234
Rep 366
Posts |
Harmonized on paper to make standards easier, but actually not in practice. UK voltages sit on the high side (230-240V) while EU voltages sit on the low side (220-230V).
I believe electricians are allowed to use the harmonized value of 230V in their calculations but have to apply a margin to it. |